An infiltrometer blower door test measures building
tightness. Tight homes tend to have excess humidity in winter; leaky homes
often have humidity problems in summer.
If there’s an indoor mold problem, all authorities agree
that the mold needs to be cleaned up.
However, mold problems can be traced to moisture problems. No moisture,
no mold growth. Identifying and
eliminating the underlying moisture source - or other cause of excess humidity
- is just as important as mold cleanup.
What does this have to do with HVAC? A lot.
While there are many moisture sources the HVAC industry isn’t
expected to diagnose or remedy - plumbing leaks, roof leaks, and exterior wall
flashing problems, just to name a few - HVAC often is the culprit for mold
growth. At the same time, it also can be the solution.
As an HVACR contractor, you really can’t just turn a blind
eye and say, “We’re not in the mold business.” You must know that HVAC
equipment creates, transforms, transports, and/or controls moisture and
humidity. Don’t try to stick your head in the sand.
An HVACR contractor must fully understand residential
moisture, ventilation, infiltration, and psychrometric issues in order to
properly serve its customers - and, stay out of mold trouble. All these air and
humidity issues also directly affect comfort and efficiency, and are opportunities
for increased sales and profits.
HUMIDIFIERS, COMBUSTION GASES
In cold climates, most leaky homes need a humidifier to
maintain the desired minimum relative humidity of 25 percent. However, there
can be too much of a good thing. Humidifiers can over-humidify a house if not
properly controlled.
In cold weather, high humidity leads to condensation on cold
surfaces, such as windows. In extreme cases, sweating and mold can also occur
on walls in stagnant areas like closets or behind furniture. If the principal
cause of the high humidity is the central humidifier, the client needs to be
educated that the indoor humidity must be lowered in very cold weather. New
controls are available that will automatically provide this feature.
Know that humidifiers can cause moisture and mold problems
when they develop water leaks. Inspecting for water leaks on maintenance and
service calls is a good idea to keep a small problem from becoming a big one.
Know, also, that combustion gases contain a lot of water
vapor. Burning 100,000 Btu of natural gas releases 1 gallon of water. If this
water is released into the home, it can lead to excessive indoor humidity and
mold. Therefore, inspect to ensure that vented gas appliances are actually venting.
Common causes of venting failure are chimney deterioration
and back drafting caused by negative pressure in the combustion appliance zone
(CAZ). Negative pressure can be caused by many things, including return duct
leaks in the CAZ, large exhaust fans, supply duct leaks outside the house,
powered attic ventilators, and basement zoning dampers.
Understanding how the house works as an interactive system
is essential for solving many back drafting and spillage problems. Correcting
them will not just get the moisture out, it will also improve IAQ by venting CO
and other combustion gases.
SEALED-COMBUSTION FURNACES
Two-pipe, 90-plus percent furnaces and power-vented water
heaters can sometimes contribute to excessive indoor humidity in the
wintertime. They send less air up the chimney, thereby creating less dry air
infiltration. This isn’t a reason to not sell them, as the higher humidity is
usually welcome in a dry home. Just be aware that it could be a contributing
factor in a home that develops excessive humidity after a change-out.
Condensing high-efficiency furnaces produce condensate,
which must be drained away. Condensate leakage can cause significant problems.
Another related moisture issue for sealed-combustion
furnaces is that in very cold climates, indoor humidity can condense on the
outside of the cold air intake pipe and drip onto items, typically in the
basement. Either insulate the pipe or reduce the overall humidity in the house.
In the winter, a leaky house tends to be a dry house, and
many are leaky. However, if a house is tight, the normal indoor-generated
moisture can become trapped, leading to high indoor humidity levels.
New homebuilders have real liabilities if they build a tight
house with poor mechanical ventilation. A blower door infiltration test will
tell you what’s going on. All homes should have mechanical ventilation
capability, and in tighter homes it should be run routinely.
An energy recovery ventilator (ERV) and/or heat recovery
ventilator (HRV) is one option. Others
include quiet exhaust fans, or outside air intakes into the return, or a
dehumidifier. Inadequate bathroom
ventilation is a common contributor to mold growth.
POOR SUMMER A/C DEHUMIDIFICATION
In many cases, the a/c system doesn’t do as good a job of
removing moisture in the summer. Common reasons include:
• Oversized a/c equipment that short cycles, reducing
moisture removal (caused by many factors).
• Higher SEER a/c equipment with lower moisture removal
capability. (Some do, but some don’t.)
• Improper a/c refrigerant charge.
• High airflow (e.g., over 450 cfm per ton in a hot, humid
climate), caused by mismatched equipment, defaulting to high speed for cooling,
and no commissioning. This leads to inadequate dehumidification and sometimes
condensate blowing off the indoor coil.
• Constant summertime air circulation, which causes
re-evaporation of moisture from the coil and drain pan, and accelerates humid
air infiltration due to duct leakage and pressure imbalances.
The answers are to size aggressively, commission properly,
and discourage constant fan in the summer.
In the summer, a leaky house is often a humid one. For most
of the Eastern United States, the summertime outside air contains large amounts
of water vapor. The infiltration of outside air in the spring, summer, and fall
can bring in significant amounts of water vapor from outside (the latent load). For example, 100 cfm of outside air at a
70° dew point will bring over 10 gallons of water into a home over 24
hours.
Whether the air comes in unintentionally through duct
leakage or the envelope, or intentionally via mechanical ventilation, the
moisture still comes in with it.
SOME CAUSES
Here are some common causes of excessive air exchange that
can lead to chronically high indoor humidity levels:
• Excessive summertime humid air infiltration, due to a
leaky house envelope.
• Excessive summertime humid air infiltration, due to a
leaky duct system.
• Negative air pressures and high infiltration rates caused,
in part, by powered attic ventilators and interior door closure.
• Infiltration at the ceiling supply duct boot to sheetrock joint.
• Moisture migration from the soil and crawlspaces.
• Excessive mechanical ventilation.
If you want to control air and humidity flows, you have to
understand how the whole house works as an interactive system. Duct sealing, in
particular, is an essential HVAC service that improves summertime humidity
control.
Be aware that if a house has high humidity in the
summertime, the answer is almost never to add ventilation. Spot ventilation for
short periods of time - from steamy bathrooms, for instance - is good. Constant
dilution ventilation, even with an ERV, can (and usually will) only make things
worse.
CONDENSATE DRAIN AND OTHER ISSUES
Insufficient a/c maintenance is a common cause of a/c
condensate drain pan overflow. Related problems are a lack of emergency drain
pans, or pans that aren’t large enough or sloped properly. Condensation on cold
attic condensate drain lines can lead to water dripping on the ceiling. The
same can happen with refrigerant suction lines due to missing rubber
insulation, which often is chewed off by rodents.
Meanwhile, condensation on ducts and air handlers in
unconditioned spaces is becoming even more common. Inadequate insulation and
unintentionally low airflow have always been key factors. Low airflow leads to
colder air in the ducts. This is now often done intentionally for enhanced
dehumidification. Unfortunately, it can lead to increased duct and air handler
sweating.
At the same time, temperatures at which the occupants keep a
home can greatly affect common moisture condensation situations. The colder the
house, and the colder the supply air temperature, the greater the chances are
of unintentional condensation on ducts, air handlers, and registers. Many
homeowners overcool their houses in an attempt to achieve comfort if their a/c
system can’t remove enough humidity.
Condensation also can occur in walls and floors that aren’t
nearly as cold as ducts or condensate drains. If the house is cooled to 68° and
the dew point of the outdoor air is 68° or higher - which is very common in the
Southeast in the summer - the entire house structure can become an evaporator
coil. If the walls are covered with vinyl wallpaper, or a floor over a
crawlspace has vinyl flooring, mold growth is almost inevitable.
The answer is to get the indoor temperature up by
controlling humidity. As stated before, this involves many possible solutions,
including duct and house infiltration sealing, enhancing a/c dehumidification,
closing damp crawlspaces, and installing supplementary dehumidification.
The drier the house, the warmer the occupants are able to
keep it at, and the less sweating problems they will have - both on their skin,
and on the house/HVAC components.
Remember: The HVAC system can be either a contributor or
solution to a moisture problem. Understand all the issues, and you’ll keep
yourself out of trouble while also increasing sales.
Sidebar: Mold Remediation
Mold remediation is not a service to offer without getting
fully trained and licensed accordingly. Be aware that, in many areas, it is
already a crowded field, and that it bears more resemblance to a general
renovation contractor than HVAC service and replacement. It should be set up as
a separate business, rather than under the same name and company.
However, even if you don’t hold yourself out to be a mold
remediation contractor, inevitably there will be times when your HVAC service
and replacement personnel come in contact with, or have to remove, moldy HVAC
components – equipment, ducts, coils, etc.
This is currently a gray area, with lots of potential for
different interpretations by licensing authorities - and, attorneys. At a bare
minimum, always ensure field personnel are issued respiratory protection. Always
take precautions when removing moldy ductwork or equipment from a home. Ensure
that it is done properly so mold spores are not disseminated.
If moldy components have to pass through the living space,
they should be double bagged. Registers and return grilles should be sealed off
before tearing out the old ducts and equipment.
Consult local state licensing authorities and your attorney
about whether your routine activities fall under laws governing mold
remediation.
Publication date: 08/13/2007